User Guide
4
COMMISSIONING WITH POWERDRIVE F300 / PUMP DRIVE F600
Dyneo
+
with Powerdrive F300 / Pump drive F600 Commissioning guide
6068 en - 2022.01 / a
Action
Description
Additional settings
Set:
• Current Reference Filter 1 Time Constant Pr 04.012 = 2 ms
• Thermal Protection Mode Pr 04.016 = Disabled (4)
• Maximum Switching Frequency Pr 05.018 = 3kH (1)
• Flux Control Gain Pr 05.027 = 0.1
• Minimum Switching Frequency Pr 05.038 = 3kH (1)
• Voltage Headroom Pr 05.041 = 5%. [Do not set a lower value. Increase this value to 10%, if the motor
is unstable in the eld weakening area].
• RFC Low Speed Mode Pr 05.064 = Injection (0)
• Saliency Torque Control Select Pr 05.065 = Auto (3) [Ensure that Pr 05.066 = High (2), otherwise
check the value entered for Pr 05.087 from the table]
• Inverted Saturation Characteristic Pr 05.070 = On (1)
• Low Speed Sensorless Mode Current Limit Pr 05.071 = 60% [Note: This forces a reduced current
limit between zero speed and 20% of motor rated speed]
If the load is a high inertia, Pr 03.010 may need to be increased.
Save parameters Select «Save Parameters» in Pr mm.000 and press the red reset button or toggle the reset digital input.
Start-up Drive is ready to start-up.