Specifications

Permissible
Fuel Metering Pump
not permissiblenot permissible
preferable
preferable
3
Visual Inspection
8
REVISION LEVEL A - 12/09/13
THE 60 SECOND VISUAL INSPECTION
1. Before starting any repairs always perform a complete a visual installation inspection. Problems resulting from an improper installation are not
warrantable issues:
a. Fuel Pump angle: Between 15 and 35 degrees- Inlet is low side, outlet is high side.
i. Yes ______
ii. No ______
iii. If not it will need to be reset to proper angle before completing repairs (pg. 26)
Figure 9
b. Combustion Exhaust (exible pipe only) - 1.5 to 2.5 inch extension past rear of cab?
i. Yes _____
ii. No _____
iii. If not it will need to be rerouted.
c. Combustion Exhaust (Flexible pipe only) - No kinks, not unwound or crushed.
i. Yes _____
ii. No _____
d. Combustion Exhaust (Flexible pipe only) - Bent at the end facing the ground at a 45 degree angle?
i. Yes _____
ii. No _____
iii. If no readjust.
e. Combustion exhaust (exible pipe only) - No low hanging areas to trap moisture.
i. Yes _____
ii. No _____
iii. If not eliminate the droop or drill 1/8 th inch hole for condensation drain.
f. Coolant lines free of obstruction, kinks or damaged?
i. Yes _____
ii. No _____
iii. If no repair as needed.
2. Verify operation; if unit runs properly complete the job otherwise continue below.
3. Turn the unit on, check diagnostic codes and utilize the troubleshooting steps listed.
The Hydronic SC can have either internal or external fuel pumps - the internal pump is preset to the correct mounting angle.