Installation manual

Motor Control Parameters
68 S1A53838 09/2011
Other Motor Control Mode Parameters
The table below lists other parameters that may need to be adjusted, depending on the setting of parameter
[Mot cont. mode sel.] (Pt).
Relationship Between [Mot cont. mode sel.] (Pt) setting and Other Motor Parameters
X: Not applicable for the [Mot cont. mode sel.] (Pt) setting
: Adjustment of this parameter is required.
O: Adjust this parameter if necessary.
Parameter Function
Parameter [Mot cont. mode sel.] (Pt) setting
01 2 34
Constant
V/Hz
Control
Variable
Torque
Control
Constant
V/Hz with
Automatic
Torque Boost
Control
Sensorless
Vector
Control
Energy
Saving
Control
uL (vL) [Motor rated freq.] ⊗⊗
uLu [Motor rated voltage] ⊗⊗
ub [Mot Voltage Boost] ⊗⊗ XXX
F170 [Mot 2 rated Freq.] OX X X X
F171 [Motor 2 rated Volt] OX X X X
F172 [Motor 2 Volt Boost] OX X X X
F400 [Auto-tuning drive] XX O OO
F401 [Slip Compensation] XX X OX
F402 [Auto Torque Boost] XX ⊗⊗
F415 [Motor rated current] OO ⊗⊗
F416 [Mot no-load current] XX O OO
F417 [Motor rated speed] OO ⊗⊗
F418 [Frequency loop gain] XX O OO
F419 [Freq. loop stability] XX O OO
F480 [No load cur. coef] XX O OX
F485 [Stall control coef. 1] OO O OO
F492 [Stall control coef. 2] OO O OO
F494 [Mot. adj coefficient] OO O OO
F495 [Motor voltage coef.] OO O OO
F496 [PWM adj. coef.] OO O OO
Code Name / Description Adjustment
range
Factory
setting
ub [Motor Voltage Boost]
0.0 to 30.0% According
to drive rat-
ing
Low speed motor torque can be adjusted with parameter ub when parameter [Mot cont. mode sel.] (Pt) (see page 67) is set
to 0 (Constant V/Hz) or 1 (Variable Torque). See curves on page 66
for more information.
If nuisance overcurrent faults occur during starting, reducing the setting of parameter ub may help.
(1) See table page 167
.