Installation manual

Diagnostics and troubleshooting
S1A53838 09/2011 153
Alarm Conditions
Alarms do not cause the drive to enter a fault condition.
Alarm Codes
Code Description Possible causes Remedies
Atn1
[
Auto tune]
Auto-tuning in process Normal if it the message disappears
after a few seconds.
CLr
[
Reset active]
This message is displayed after the
STOP key is pressed while an detected
fault is displayed.
Press the STOP key again to clear the
detected fault.
db
[
DC braking]
DC braking in process The alarm code goes off in several
seconds if no trouble occurs.
dbOn
[
dbOn]
Motor shaft fixing control
E-17
[
HMI error]
A graphic display option key has been
held down for more than 20 seconds.
A graphic display option key may not be
operating properly.
Release the graphic display option
key.
If this does not clear the error, replace
the drive.
EI
[Excess value]
The number
of digits that can be
displayed has been
exceeded
The number of digits entered for values
such as frequencies is more than 4 (the
upper digits have priority).
Lower the frequency free-unit
magnification [Customized freq val]
(F702).
EOFF
[
Loc. Stop en.]
The operation panel is used to stop the
operation in automatic control or remote
control mode.
Press the STOP key for an emergency
stop. To cancel the emergency stop,
press any other key.
Err1
[
Speed ref alarm]
The frequency setting signals at points 1
and 2 are set too close to each other.
Set the frequency setting signals at
points 1 and 2 apart from each other.
h999
[Pin&1MWh]
Integral input
power
Integral input power is more than
999.99 kWh.
Press and hold down the ENT key for
3 s or more when power is off or when
the input terminal function CKWH is
turned on or displayed.
H999
[Pout&1MWh]
Integral
output power
Integral output power is more than
999.99 kWh.
Press and hold down the ENT key for
3 s or more when power is off or when
the input terminal function CKWH is
turned on or displayed.
HEAd
End
[Head]
[End]
Display of first/last data
items
The first and last data item in the auh
data group is displayed.
Press MODE key to exit the data
group.
H1
LO
[High]
[Low]
Parameter adjustment
error
During programming, a value was
entered that exceeds the maximum or
minimum value of the parameter.
Enter a value within the bounds of the
parameter
InIt
[
Initialization]
Parameters are being initialized to
default values.
Normal if the message disappears
after several seconds.
LStp
[Low speed stop]
Auto-stop
because of continuous
operation at the lower-limit
frequency
The automatic stop function selected
with F256 was activated.
To deactivate the automatic stop
function, increase the frequency
command above the lower-limit
frequency LL+F391 or turn off the
operation command.
NOFF
[
Line undervolt flt]
The phase-to-phase input voltage is too
low.
Measure the main circuit supply
voltage. If the voltage is at a normal
level, the drive requires repair.
OFF [Drive stop]
The ST-CC (run permissive) circuit is
open.
Close the ST-CC circuit.
nSt [Lock State]
The Li is already active when the function
is validated.
The Li is already active when a
configuration transfer is done with the
function is validated.
Deactivate the active Li configured.
rtrY
[
Auto reset]
The drive is in the process of restart.
A momentary stop occurred.
The drive is operating normally if it
restarts after several seconds.
StOp
[Stop supply]
Momentary
power loss slowdown stop
prohibition function
activated.
The slowdown stop prohibition function
set with F302 (momentary power loss
ride-through operation) is activated.
To restart operation, reset the drive or
input an operation signal again.