Installation manual

Diagnostics and troubleshooting
152 S1A53838 09/2011
OH
[Drive
overtemperature]
The drive cooling fan is not working.
The ambient temperature is too high.
An enclosure air vent is blocked.
A heat source is too close to the drive.
The drive heatsink temperature sensor is
malfunctioning.
Restart operation by resetting the drive
detected fault after cool-off.
Decrease the ambient temperature by
increasing the free space around the drive
and removing any heat generating source
from the proximity of the drive.
Check the fan operation
OH2
[PTC overheating]
The external PTC embedded in the motor
windings indicates a motor overtemperature
condition.
Correct the motor overload condition.
Check the PTC for correct operation.
OL1
[Drive overload]
The acceleration time is too short.
The DC injection current level is too high.
The setting of parameter [Mot cont. mode
sel.] (Pt) is incorrect.
The drive is starting into a rotating load.
The load is too large.
Increase the acceleration time parameters
(ACC or F500).
Reduce the setting of parameters F251
and/or F252.
Select the correct setting for parameter [Mot
cont. mode sel.] (Pt).
Enable catch on the fly, parameter F301.
Set parameter F302 to 2.
Use a drive with a higher power rating.
OL2
[Motor overload]
The setting of parameter [Mot cont. mode
sel.] (Pt) is incorrect.
The motor is jammed.
Low-speed operation is performed
continuously
Excessive load is applied to the motor.
Select the correct setting for parameter [Mot
cont. mode sel.] (Pt).
Check the load.
Adjust parameter OLM to the overload level
that the motor can withstand during low
speed operation.
OP1
[Overvoltage
acceleration]
The input voltage is fluctuating abnormally.
Power network is greater than 200 kVA.
Power factor capacitor switching
SCR switching on power network
The drive is starting into a rotating load.
Intermittent output phase fault
Install a line reactor.
Enable catch on the fly, parameter F301.
Set parameter F302 to 2.
Determine the cause of the missing output
phase (such as a bad connection, an output
disconnect, or an open winding in the motor)
and rectify the trouble.
OP2
[Overvolt.
deceleration]
The deceleration time is too short.
Overhauling load
The input voltage is fluctuating abnormally.
Power network is greater than 200 kVA
Power factor capacitor switching
SCR switching on power network
The drive is starting into a rotating load.
Intermittent output phase fault
Increase the deceleration time parameters
(DEC or F501).
Enable parameter F305.
Install a line reactor.
Check the input and output circuits for phase
loss detection and rectify.
Enable catch on the fly, parameter F301.
OP3
[Overvoltage cont.
speed]
The input voltage is fluctuating abnormally.
Power network is greater than 200 kVA
Power factor capacitor switching
SCR switching on power network
The drive is regenerating - the load causes
the motor to run at a frequency higher than
drive output frequency.
Intermittent output phase fault
Install a line reactor.
Check the input and output circuits for phase
loss detection and rectify.
Ot
[Overtorque]
The calculated motor torque has reached
the level set by parameter F616.
Adjust the settings of parameters F615
and F616 as needed.
Verify machine operation.
SOUt
[PM motor step-out]
(permanent magnet
motor pulls out of
synchronism)
The motor is jammed.
Output phase loss
Impact load
Check the load and correct the jammed
condition.
Check the condition of the motor and load
wiring.
UC
[Underload]
The measured motor current has dropped
below the level set by parameter F611.
Check parameters F610612 for the
correct settings.
UPI
[Undervoltage]
The input voltage is too low. Check the input voltage and rectify the
trouble.
Select the correct setting for parameter
F627.
Enable catch on the fly, parameter F301.
Set parameter F302 to 2.
Code Name Possible causes Remedies