Display Parameters
120 S1A53838 09/2011
Display parameters
Code Name / Description Adjustment range Factory setting
F710 [Displayed param.]
Default graphic display option operational value 0 to 10 0
0
1
2
3
4
5
6
7
8
9
10
[Motor frequency] Motor operating frequency (Hz or custom display), see [Customized freq val] (F702) on page 121
.
[Reference] Speed reference (Hz or custom display), see F702 on page 121
.
[I Mot] Motor current (% or A), see [Unit value selection] (F701) below.
[Drive rated I] Drive rated current (A)
[Drive therm state] (%)
[Motor power] Output power (kW)
[Int speed ref] Internal speed reference (after PID function) (Hz or custom display, see F702 on page 121
.
[Com data] Serial communication data
[Motor speed] Output speed (rpm, see [Motor rated speed] (F417) on page 70
)
[Com count] Displays the total number of frames received by the communication card since the last power ON
[Com count norm st.] Displays the total number of valid frames received by the communication card since the last power ON
The setting of parameter [Displayed param.] (F710) determines the default display on the drive’s embedded display terminal
upon power up.
Status alarms C, P, L, and H can only be displayed on the graphic display option if [Displayed param.] (F710) is set to 0. See
“Run Mode” on page 23
for more information.
F701 [Unit value selection]
Unit value selection - 1
0
1
[%]
[Amp or Volt]
The setting of parameter F701 determines how certain values will be displayed on the drive embedded display terminal, either
as a percentage of the drive rating or as a value of amperes or volts as appropriate.
The setting of F701 will only affect parameters and display values that can be represented in amperes or volts. This includes
the following parameters:
[Motor thermal prot.] (tHr) and F173: motor rated current
F251: DC braking current level
F185 and F601: motor current limit
F611: underload detection level
Motor rated voltage (parameters ulu and F171) are displayed in volts.
F708 [Display ref. resol.]
graphic display option Frequency Resolution - 0
0
1 to 255
Disabled - 0.1 Hz steps
See the formula below
Parameter F708 works along with parameter [Loc. speed ref. step] (F707) (see page 77
) to adjust the incremental steps of
the drive embedded display terminal frequency display.
At its factory setting, parameter F708 is disabled and the embedded display terminal increments or decrements frequency dis-
plays in 0.1 Hz steps.
If parameter F708 is set to a value other than 0, then the embedded display terminal frequency display is determined as fol-
lows: embedded display terminal frequency display = Internal speed reference (after PID function) x F708 / F707
For example, if both F707 and F708 are equal to 1, the embedded display terminal frequency display will increase only in
1 Hz steps.
F621 [Run time alarm]
0.0 to 999.9 610.0
(6100 hours)
Parameter F621 is used in conjunction with a relay output set to functions 42 or 43 (see page 102) to signal that the run time
specified by the setting of F621 has accumulated.
0.1 = 1 hour, 100 = 1000 hours
F748 [Power cons. memo]
Accumulated power consumption memory - 1
0
1
[Disable]
[Enable]
The setting of parameter F748 determines whether the drive’s accumulated power consumption memory, displayed in kilowatt-
hours (kWh), is cleared when the line power is cycled. If F748 is set to 0, the memory is cleared. If set to 1, the kWh memory
is retained.