Installation manual
I/O Control Parameters
108 S1A53838 09/2011
Code Name / Description Factory setting
F200 [Auto/man speed ref]
Auto/Manual Speed Reference Switching 0
0
1
[Enable]
[Disable]
Switching between two speed reference sources by means of a logic input is enabled if parameter F200 is set to 0.
To use this function, you need to assign a logic input to function 38, Auto/Man speed ref.
When the assigned logic input is off, the drive will follow the speed reference source defined by parameter [Frequency mode sel]
(FMOd) (see page 77
).
When the assigned logic input is on, the drive will follow the speed reference source defined by parameter [Remote spd ref 2]
(F207) (see page 78
).
When parameter F200 is set to 1, the drive will follow the FMOd speed reference source when it is operating above 1 Hz.
Below 1 Hz, it will follow the F207 speed reference source.
FMSL
[AO funct. selection]
Analog Output Function Selection 0
FM [AO scaling]
Analog Output Scaling -
Parameter FM is used to match the FM terminal output signal with the input requirements of the attached panel meter by adjust-
ing the slope and bias of the analog output signal. Before adjusting FM, set [AO funct. selection] (FMSL) to either 15 or 17.
As you adjust the value of FM, monitor the display on the attached panel meter. When the meter display reaches 100%, press
the ENT key on the drive embedded display terminal. The drive will flash between FM and the adjusted value, indicating that the
adjustment has been saved.
Value Function Maximum Signal
0 [Motor frequency]: Output frequency
[Max frequency] (FH)
1 [Motor current]: Output current 150 % of [Motor current]
2 [Speed ref]: Speed reference
[Max frequency] (FH)
3 [DC bus U]: DC bus voltage 150 % of [DC bus U]
4 [Motor U]: Output motor voltage 150 % of [Motor U]
5 [Input power]: Input power 185 % of [Input power]
6 [Output power]: Output power 185 % of [Output power]
7 [motor torque]: Estimated motor torque 250 % of rated motor torque
8
[Torque I]: Motor torque current Current at 250 % of rated motor torque
9
[Motor thermal]: Motor thermal state 100 % of motor’s rating
10
[Drive thermal]: drive thermal state 100 %
11
[Do not use]: DO NOT USE -
12
[Internal reference]: Internal speed
reference (after PID)
[Max frequency] (FH)
13 [VIA]: VIA input value Maximum input value
14
[VIB]: VIB input value Maximum input value
15
[Fixed 100%]: Fixed output – 100% signal
(Selection 1 – output current)
-
16
[Fixed 50%]: Fixed output – 50% signal
(Selection 1 – output current)
-
17
[Fixed 100%]: Fixed output – 100% signal
(Selections 0, 2, 3, 4, 5, 6, 7,
8, 9,10, 12, 13, 14, 18)
-
18
[Com data]: Serial communication data FA51 = 1000
19
[Do not use]: DO NOT USE -